temperature at startup of VWL 75/6 #1359
-
When my heatpump is started, the ZWZ AI indicates a desired value for the water temperature to the heating circuit. So far I have not been able to find the required line in the ctlv2 configuration file to log this setpoint. Once the pump is running the setpoint is gradually lowered (modulation) to match the setpoint given by the heating curve. |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 4 replies
-
Hi, ebusctl read Status01 current temp 39 |
Beta Was this translation helpful? Give feedback.
Hi avanmourik,
the line is not in 8.hmu, it is in include file hcmode.inc
HC Betriebsart2,,,,,,,,,,,,,
*r,,,,,,"B511",,,,,,,
*uw,,,,,,"B510",,,,,,,
uw,,SetMode,Betriebsart,,,,00,,,hcmode,,,,flowtempdesired,,temp1,,,,hwctempdesired,,temp1,,,,hwcflowtempdesired,,temp0,,,,,,IGN:1,,,,disablehc,,BI0,,,,disablehwctapping,,BI1,,,,disablehwcload,,BI2,,,,,,IGN:1,,,,remoteControlHcPump,,BI0,,,,releaseBackup,,BI1,,,,releaseCooling,,BI2,,,,
#potential last byte: currentmode,s,UCH,0=off;1=standby;2=heat;3=water,,
r,,Status01,Vorlauftemperatur/Rücklauftemperatur/Aussentemperatur/WW Temperatur/Speichertemperatur/Pumpenstatus,,,,01,,,temp1;temp1;temp2;temp1;temp1;pumpstate,,,
r,,Status02,Betriebsart/Maxi…